I have a Lennox G26-75. Burners fire up fine, but fan in automatic mode doesn't kick in. After a minute or 2, the burners go out. If I put fan in manual mode, burners go on & stay on until desired temperature is reached. What's needed??Post created: 2012-12-30 Type of Equipment: Furnace Views: 44This question was created on the page: http://www.furnacecompare.com/furnaces/lennox/g26.html. I have a Lennox G26-75. Burners fire up fine, but fan in automatic mode doesn't kick in. After a minute or 2, the burners go out. If I put fan in manual mode, burners go on & stay on until desired temperature is reached. What's needed?? On 2012-12-30 Bruce wrote: Addiing to my previous question---I recently replaced the Johnson ignition control unit with the new Lennox OEM 30W33 ignition control kit and flame sensor. Could it be misfired? On 2012-12-30 Bruce wrote: I meant to say "miswired." On 2012-12-30 wrote: sounds like your problem was not the electronic ignition, but sounds like the blower control board bcc3
On 2012-12-30 Bruce wrote: Thanks, I'll check it out. On 2013-01-06 Bruce wrote: I just received my new BCCE blower control board & installed in about 1/2 hr. It works great! Thanks for your help. Your Answer |