I have a Lennox G26-75. Burners fire up fine, but fan in automatic mode doesn't kick in. After a minute or 2, the burners go out. If I put fan in manual mode, burners go on & stay on until desired temperature is reached. What's needed??

Post created: 2012-12-30 Type of Equipment: Furnace Views: 44

This question was created on the page: http://www.furnacecompare.com/furnaces/lennox/g26.html.

I have a Lennox G26-75. Burners fire up fine, but fan in automatic mode doesn't kick in. After a minute or 2, the burners go out. If I put fan in manual mode, burners go on & stay on until desired temperature is reached. What's needed??


On 2012-12-30 Bruce wrote:

Addiing to my previous question---I recently replaced the Johnson ignition control unit with the new Lennox OEM 30W33 ignition control kit and flame sensor. Could it be misfired?


On 2012-12-30 Bruce wrote:

I meant to say "miswired."


On 2012-12-30 wrote:

sounds like your problem was not the electronic ignition, but sounds like the blower control board bcc3


On 2012-12-30 Bruce wrote:

Thanks, I'll check it out.


On 2013-01-06 Bruce wrote:

I just received my new BCCE blower control board & installed in about 1/2 hr. It works great! Thanks for your help.