I need the meaning of the diagnostic light codes on the control board of a Lennox Elite SeriesPost created: 2012-11-14 Type of Equipment: Furnace Views: 121This question was created on the page: http://www.furnacecompare.com/furnaces/lennox/elite.html. 4 blinks on control board . Both fans run when powered with no thermostat wires connected . New board witch worked fine for 1 month On 2012-11-15 JB wrote: To be absolutely sure what this means you will also need to know the model number. If you know the model number you can find documentation here: http://www.lennox.com/support/literature.asp
The following is for the Lennox EL195:
Lennox EL195 Error Codes
Off: No power to control or board fault detected Heartbeat: Control powered − displayed during all modes of operation if no errors are detected 1: Reverse Line Voltage Polarity 2: Improper Earth Ground 3: Burner failed to light, or lost flame during heat demand 4: Low Flame Signal − check flame sensor 5: Watchguard − burner failed to light, exceeded maximum number of retries or recycles. 6: Ignitor Circuit Failure − not available on this control 7: Primary or Secondary Limit Open or Watchguard Mode − Limit Switch Open longer than 3 minutes 8: Rollout Switch Open 9: Pressure Switch failed to close or opened during heat demand 10 Watchguard − Pressure Switch opened 5 times during one heat demand 11 Pressure Switch stuck closed prior to activation of combustion air inducer 12: Flame Sensed without gas valve energized 13: Low Line Voltage
Notes Note: A "Heartbeat" is indicated by a "Slow Flash" − 1 sec on 1 sec off, repeating Note: Error codes are indicated by a "Rapid Flash" − the LED flashes X times at 1/2 sec on 1/2 sec off, remains off for 3 sec, then repeats Note: Last 10 error codes are stored in memory − To recall, press and release button, most recent will be displayed first, LED off for 3 sec, then next error code is displayed, etc. To clear error codes, depress and hold button longer than 5 seconds.
To keep legal happy, let me just say that I am not an HVAC contractor, and you should never even look at your furnace without having a qualified, liability accepting HVAC contractor present. To keep sales happy, let me just say that you can find an HVAC contractor that's happy to take your money here: http://www.furnacecompare.com/perl/find_contractors.pl
Your Answer |